Hi, seeking knowledge, or at least reasonable guesses
. Which would you install for house bank battery protection, single use sacrificial fuses or re settable circuit breakers ?
The battery bank in question is made up with 6 volt golf cart batteries wired in series/parallel.
I am looking at installing 100 amp protection per pair of batteries.
Cheers Bob.
Single use sacrificial fuses, only because it's a boat and it can / will get wet. And also it's much more fun searching for spare fuses in the dark than flicking a switch.![]()
Definitely fuse for that application.
www.outbackmarine.com.au/fuse-midi-ami-100a?gclid=EAIaIQobChMItrKh9cjU2gIVBeC9Ch11MAqPEAQYAyABEgKi9_D_BwE
Blue Sea Fuse holders and fuses available from Whitworths.
Hi Bob remember you are only protecting the wire from your house battery to your switchboard, if the wire will only take 50amps then you need to fuse at or below that wires limit.
Hi Bob remember you are only protecting the wire from your house battery to your switchboard, if the wire will only take 50amps then you need to fuse at or below that wires limit.
What would roughly be the amps a 10mm dia battery lead carry???
Dont know why you would run a cable that big to a switchboard from your house batteries, not much point in putting a fuse in that, If you have a dead short in your house batteries you will blow the crap out of everything that it feeds. What are you running ? the decklights on the Titanic?
Hi Bob remember you are only protecting the wire from your house battery to your switchboard, if the wire will only take 50amps then you need to fuse at or below that wires limit.
What would roughly be the amps a 10mm dia battery lead carry???
10mm2 cable, about 60amp.
Also ithe fusei is not only protecting the cable but also the switchboard up to the line side of the protective devices.. you need to size your fuse to the cable rating or the switchboard rating which ever is the lesser. eg. If the switchboard is only rated at 40amps and the cable is rated at 60amps, you can only use a 40amp fuse. Another thing you need to take into consideration is voltage drop which is considerable with 12vdc. If you cable is a fair length your 10mm2 cable might only be good for 30amps. The last thing you want in a boat is voltage drop. If you are unsure about cable size alway go bigger, but don't increase your fuse size.
For example the calculated cable size in my caravan from my 315Ahr Lithium battery to the battery management system is 240mm2 cable and the length is only 3m. This is to give me next to no voltage drop with a 200amp load. This cable has a continuous rating of over 400amps but is protected with only a 200amp fuse. The cable size is for voltage drop purpose, not its current carrying abilities.
PS. what Littleweie said about blowing things up is rubbish as this is down stream protection for the sub main cable and switchboard and all you other equipment should have smaller protection which in turn protects it.
The cable size quoted was 10mm diameter, That would take much more than 60 amps I would think, Im not a expert but he needs to protect the wire feeding his switchboard from his house bank. if he chooses not to (as this part of the wiring is often neglected with fuse protection) he risks a possible fire in a dead short situation.
The cable size quoted was 10mm diameter, That would take much more than 60 amps I would think, Im not a expert but he needs to protect the wire feeding his switchboard from his house bank. if he chooses not to (as this part of the wiring is often neglected with fuse protection) he risks a possible fire in a dead short situation.
As I said the cable and switchboard must be protected. Cable is not measured in diameter ( except some small automotive cable), it is measured in cross sectional area. If the conductor measured about 10mm across the conductor it would be about 50mm2 cable giving it a rating of about 150amps. A fuse will not protect from a dead short with in a battery, nothing will. But I don't think I have ever heard of a dead short with in a battery. A fuse only short circuit protect and over current protect down stream of the fuse but will over current protect up stream. When we get into the bigger stuff we can get fault currents that can blow up the batteries but we then user fault current limiting fuses which in my caravans case are special fast blow fuses. I am trying to make this sound as simple as I can in layman's terms. My specialty for the last 40 years is the design, building and installing large switchboards.
I think he is putting fuses on all positive battery cables as Using 6 volt batteries you will have some in series parralleled up with the others. That way if you f@ck up with a termination the big blue flash will not escape. You are only protecting the batteries from a dead short after the fuses. Fuses to the switchboards are a different matter.
The cable size quoted was 10mm diameter, That would take much more than 60 amps I would think, Im not a expert but he needs to protect the wire feeding his switchboard from his house bank. if he chooses not to (as this part of the wiring is often neglected with fuse protection) he risks a possible fire in a dead short situation.
As I said the cable and switchboard must be protected. Cable is not measured in diameter ( except some small automotive cable), it is measured in cross sectional area. If the conductor measured about 10mm across the conductor it would be about 50mm2 cable giving it a rating of about 150amps. A fuse will not protect from a dead short with in a battery, nothing will. But I don't think I have ever heard of a dead short with in a battery. A fuse only short circuit protect and over current protect down stream of the fuse but will over current protect up stream. When we get into the bigger stuff we can get fault currents that can blow up the batteries but we then user fault current limiting fuses which in my caravans case are special fast blow fuses. I am trying to make this sound as simple as I can in layman's terms. My specialty for the last 40 years is the design, building and installing large switchboards.
OK, you have got me thinking now. Boat has three pairs of 6 volt house batteries each connected to a common power post thence to a three way switch (1 2 both off) thence to the switch board where all circuits are individually fused with appropriate sized fuses. Currently no fuses between batteries and switch board. Cables to three way switch are heavy battery cable capable of carrying power to start the motor should it ever be required (never has to date but who knows).
I guess I need recommendations as to how to best proceed to improve the safety of the system between batteries and switch board.
Thanks in advance, Bob.
I think he is putting fuses on all positive battery cables as Using 6 volt batteries you will have some in series parralleled up with the others. That way if you f@ck up with a termination the big blue flash will not escape. You are only protecting the batteries from a dead short after the fuses. Fuses to the switchboards are a different matter.
Chris, thanks, now you have me worried about letting the big blue flash escape. ![]()
Don't forget to allow for starter load for that one time when your engine battery has died...........
Don't forget to allow for starter load for that one time when your engine battery has died...........
Yeah, that's part of the dilemma.
Hi UncleBob
i assume you have 2 parallel sets to terminal number 1 and 1 parallel set to terminal number 2 and the switch is adjacent to the batteries. From the common on the switch you have 2 cables, one to the starter Motor (large cable) and one to the switchboard (smaller cable). The charging cables also come back to the common terminal, possibly via the motor cable.
On most smaller boats they don't fuse between the batteries and the changeover switch and in a lot of cases don't fuse between the switch and switchboard and motor (which sounds like you case)
In your case I would leave the cables from the batteries to the switch and switch as is and then install a 50amp fuse on the cable that goes to the switchboard, provided the cable is large enough. The starter cable should be fused ( but in most cases are not) with a fuse that will withstand the starting current of the motor.
PS I am assuming you don't have a seperate motor starting battery.
Hope this is of some help as I am assuming a lot of things.
John
Hi UncleBob
i assume you have 2 parallel sets to terminal number 1 and 1 parallel set to terminal number 2 and the switch is adjacent to the batteries. From the common on the switch you have 2 cables, one to the starter Motor (large cable) and one to the switchboard (smaller cable). The charging cables also come back to the common terminal, possibly via the motor cable.
On most smaller boats they don't fuse between the batteries and the changeover switch and in a lot of cases don't fuse between the switch and switchboard and motor (which sounds like you case)
In your case I would leave the cables from the batteries to the switch and switch as is and then install a 50amp fuse on the cable that goes to the switchboard, provided the cable is large enough. The starter cable should be fused ( but in most cases are not) with a fuse that will withstand the starting current of the motor.
PS I am assuming you don't have a seperate motor starting battery.
Hope this is of some help as I am assuming a lot of things.
John
John, thanks very much for your input, your assumptions are mostly correct except that there is another pair of 12 volt batteries dedicated to the engine start and windlass, there are a pair of three way switches wired together in parallel, that is hot wire from house bank to terminal 1 on both switches, wire from start/windlass bank to terminal 2 on both switches (enables all loads to be taken from either battery) with alternator output to start battery via engine pos lead and both banks connected via a vsr, wired to connect only when engine is running.
Typically all house loads are connected to switch #1 common from where the source of power can be selected from bank of choice, engine/windlass is connected to switch #2 common where similarly power can be taken from either bank.
There is 190 watts of solar connected via a morningstar duo charge pwm controller that keeps everything charged.
You are correct in that there are no fuses in the battery leads at all or in the wire to the switchboard. This is what my concern is.
Once again, thanks. Bob.
Dont know why you would run a cable that big to a switchboard from your house batteries, not much point in putting a fuse in that, If you have a dead short in your house batteries you will blow the crap out of everything that it feeds. What are you running ? the decklights on the Titanic?
I'm not running a wire that big to my switchboard - I was just asking regarding another location!!